CASE 963454
Goals and Symptoms:
OFS 3.3 running on Server 2003 connected to Momentum PLC via Ethernet showing errors. Concept on same Server. OFS pointed to .PRJ file. Appears to not be able to synch with PLC.
Please find attached 2 commented OFS verbose of errors. Robert Willis of Schneider is familiar with this problem as he assisted last Friday in troubleshooting. Today I registered C:\Concept\CC2CAT.EXE successfully but the symptom are the same.
Causes and Fixes:
We reproduced the errors with the same configuration.
05/01 15:41:13 453ms : NA : Sent Request : 00100000 0005012A Length = 11 bytes at TC = 1458734 (Tid = 255.16.23081520)
05/01 15:41:13 453ms : NA : _____________ : 010400
05/01 15:41:13 515ms : NETMAN : Answer received : 00100000 000B012A Length = 17 bytes at TC = 1458765 (Tid = 255.16.23081520)
05/01 15:41:13 515ms : NETMAN : ______________ : 0104004D 54000000
05/01 15:41:13 515ms : NETMAN : ______________ : 00
05/01 15:41:13 515ms : NETMAN : Request Treat Time Network 31 Ofs 62
05/01 15:41:13 515ms : MODBUS : (Refresh 0002) reload symbol table and update items for device MBT 139.160.234.13;1
05/01 15:41:13 515ms : SdkConcp : ReloadAndUpdateSymbols, ApplicationName mismatchSdkConcp : <-> MMT
05/01 15:41:13 515ms : MODBUS : Inconsistency detected with MBT 139.160.234.13;1
05/01 15:41:13 515ms : MODBUS : Inconsistent project name for MBT:139.160.234.13;1 : unlocated support suppressed
05/01 15:41:13 515ms : MODBUS : Inconsistency ignored for Device MBT:139.160.234.13;1
The problem occurred when we changed the Momentum firmware (M1ev126e.bin) for Concept XL V2.6 SR4. With the previous firmware (M1ev122e.bin), it works fine.
If you want to resolve this problem rapidly, I suggest you to downgrade the firmware version of Momentum to M1ev122e.bin. (use the EXECLoader tool to downgrade the firmware)